Post by WECON Technical support on May 18, 2016 6:44:40 GMT
|
|
|
Post by framirez on Oct 4, 2016 14:06:31 GMT
Hi Jason
This example is based on HMI Levi 777 A model. And what happened if I`m using Levi 350 T model?. Due to my PLC is a LX3V 0806 MR type, and it COM port is only RS 485 type, not RS422 standard. And, it posible that you send us the PLC program relationed with this HMI file : "communicate with WECON PLC". So can will see, the settings used on the PLC editor.
Best Regards
|
|
|
Post by WECON Technical support on Oct 8, 2016 5:53:30 GMT
Syetem PLC ports-PD.zip (588.19 KB) LX3V-0806 PLC can not support COM1 RS485 port,If you want to use COM2 RS485 conmunication with HMI by wecon PLC protocol.You need set communication parameters just like the document.
|
|
|
Post by bluebox on Sept 15, 2017 2:59:46 GMT
Is there any plans to add support for Rockwell DF1 protocol to the Levi HMI panels?
|
|
|
Post by WECON Support on Sept 16, 2017 1:23:06 GMT
You could find AB DF1 protocol in the leviu studio. Please check again. both in com1 and ethernet.
|
|