Post by WECON Technical support on Oct 12, 2016 5:52:43 GMT
Ⅰ ReasonThe following reasons will cause HMI crash/freeze. - The non-English code in the software install path and project path, if those path contain other language code, like Spanish, Russian, and so on, when download project from software to HMI, it will cause HMI crash. The path of software and project only supports English.
- HMI version is different with software version. For example, you are using English software (LeviStudio), but you HMI are in Unicode version, if your project screens contain non-English characters, when you download project to HMI, the HMI will crash. If you are using Unicode software (LeviStduioU), but your HMI are in English version, when you download project to HMI, HMI will crash.
- Old Version: Vx.x.xx-P: multiLan yyyy-mm-dd, it means HMI is English version. Unicode version: Vx.x.xx-P: Unicode yyyy-mm-dd, it means HMI is Unicode version. Please connect HMI to software and click “HMI version” in download windows to check HMI version.
Ⅱ Solution If the HMI crash by above reasons, it can be repaired by clients. Please try the following steps: Step 1. remove the power; Step 2. power holding in the bottom left corner of the screen. Step 3. it will display "please download a new project" after 10 seconds Step 4. connect HMI to LeviStudioU, download project again, and updating os.
|
|
|
Post by evenchu on Jul 23, 2018 15:48:04 GMT
Hi...I am using WINCC V6.0 SP3 HMI baseoperator station and one S7-412 (6ES7 412-2XJO5-OABO) PLC.The Communication Link between WINCC HMI & PLC is via MPI port using CP5611.Some time WINCC HMIfreezes/crashes 3 or 4 time in a dayafter 7 or 8 hour interval, as a result reading in HMI I/O fields show maximum limits. after freezes/crashes HMI i need torestart the operator station every time then station is capable againfor smooth operation. prototype pcb assembly china
|
|
|
Post by WECON Support on Jul 25, 2018 2:33:20 GMT
wincc v6.0 sp3 hmi is siemens hmi , not wecon hmi. I don't konw why it will crash. I think you should ask someone in siemens forum.
|
|