Post by sawanpatil on Jul 25, 2015 7:51:13 GMT
I want to control frequency of danfoss vfd micro drive model with wecon plc LX3V-2416MT-A trough 485BD someone help me.
|
|
|
Post by WECON Technical support on Jul 25, 2015 8:45:38 GMT
|
|
|
Post by daniel94 on Jan 19, 2017 21:52:16 GMT
im controlling a VFD YASKAWA through modbus, im using port COM2 to send data to VDF. I can write a single register like frequency and i can read register like frecuency, voltage, current. But my problem is like i could send a bit from PLC to VFD. For example in VFD yaskawa the register modbus is 0001h and that register have 0-F bits.For example bit 0 is run, bit 1 reverse, bit 3 fault reset. How can i write this register in the VFD? ? Attachments:
|
|
|
Post by WECON Technical support on Jan 20, 2017 1:30:48 GMT
One word is grouped by 16 bits. If you want bit0=1.You just write a value 1 into 0001h. If you want bit1=0/1.You just write 0/2 into 001h If you want bit3=0.You just write 0 into 001h.
if you want bit0=1,bit1=0,bit3=0.You just write 0001(2)=1(10) into 001h. if you want bit0=1,bit1=1,bit3=1.You just write 0011(2)=3(10) into 001h.
You can use a M register to control Mov instruction which can send a value to D register.Then send D value to Modbus address.
|
|
|
Post by daniel94 on Jan 20, 2017 1:59:56 GMT
yes i tried but i cant. ..im using instruction RS its the correct instruction ?? but using instruction mov how? ? please could you give an example..how can i write in modbus addres? ?? please give an example . thank you
|
|
|
Post by WECON Technical support on Jan 20, 2017 2:48:42 GMT
Please check the modbus rtu demo.I use M0 and M1 to write different value into Mdobus slave 1. PLC- Modbus master.wcp (42.42 KB) The communication paremeter is COM2 Rs485 9600 1 8 None
|
|
|
Post by daniel94 on Jan 20, 2017 16:40:49 GMT
i tried to do it, but the VFD dont respond
|
|
|
Post by daniel94 on Jan 20, 2017 17:03:52 GMT
im sorry was a mistake mine, the VFD its working. Thank you
|
|
|
Post by WECON Technical support on Jan 21, 2017 2:26:46 GMT
im sorry was a mistake mine, the VFD its working. Thank you No problem,You are welcome.
|
|
|
Post by bdmail4 on Oct 25, 2017 14:42:26 GMT
dear sir please post a video tutorial about wecon lx3v plc to vfd modbus Rtu ( LS,DELTA,Siemens,Omron ETC ).
|
|
|
Post by WECON Technical support on Oct 27, 2017 2:29:57 GMT
dear sir please post a video tutorial about wecon lx3v plc to vfd modbus Rtu ( LS,DELTA,Siemens,Omron ETC ). Hi thanks for supporting wecon technology . All the video already upload to YouTuBe , the link as below , www.youtube.com/user/Wecon2004/videos.
|
|
|
Post by sukhooraay on May 19, 2020 23:06:56 GMT
Hello Admin, Please share program/setting for: Wecon inverter (vfd) connect to HMI and plc youtu.be/JIcGSclrVlgThank You
|
|