Post by petri on May 30, 2019 14:55:25 GMT
Hi
I have a problem with setting frequency via Modbus RTU in Inverter 8000B. I've set in 8000B : - Control command source: F0.01 = 2 (Communications RS485) - Master frequency source X: F0.03 = 9 (Communication interface) To set inverter frequency by LX3VP I"m using 06H protocol function and 2000H address with frequency value. I can see on the inverter display panel that it takes frequency from LX3VP. But when I send control command at 1000H address: Forward (01H) or Reverse (02H) or JOG forward (03H) or JOG reverse (04H) inverter runs always with minimum speed about 1.3 Hz.
|
|
|
Post by gavra on May 31, 2019 20:12:52 GMT
Hello Petri,
I think You should send frequency to the F0.08 parameter.
I am working with modbus with some similar regulators like 8000B, and it works like this way.
Bye
|
|
|
Post by WECON Support on Jun 17, 2019 3:03:58 GMT
Hi
I have a problem with setting frequency via Modbus RTU in Inverter 8000B. I've set in 8000B : - Control command source: F0.01 = 2 (Communications RS485) - Master frequency source X: F0.03 = 9 (Communication interface) To set inverter frequency by LX3VP I"m using 06H protocol function and 2000H address with frequency value. I can see on the inverter display panel that it takes frequency from LX3VP. But when I send control command at 1000H address: Forward (01H) or Reverse (02H) or JOG forward (03H) or JOG reverse (04H) inverter runs always with minimum speed about 1.3 Hz.
Hello Petri, Please set the frequency for Invertor as Gavra said.
|
|